Installing GFCI but don't want downstream protection
Hi all - I think this is the best forum to post this on. I've posted this same question at one of the Garden Web sites, but I figured many here would probably know the answer as well.
I want to install a GFCI outlet for my fish tank, but don't want downstream protection. Can I just take the black, white, and ground wires at the outlet I am replacing, splice them together (black to black, and white to white, of course :-) ), then connect jumpers from those splices which I then attach to the "line" and ground terminals of the GFCI outlet? Is this a valid installation? Thanks! |
01/05/2008, 04:38 PM | #2 |
Registered Member
Join Date: Jan 2005
Location: Utah
Posts: 120
|
Yes, just wire to the line side only and not use the load side.
|
|
|