Battery backup to prevent lighting from blowing circuit?

I live in an apartment building and come home about every other day to find the circuit to my tank blown.

I hope someone can give me some ideas...I've had some close calls..

Sometimes when my lights switch on the initial startup blows the fuse. Would a battery backup fix this? If this would fix it Iwould lose the functionality of my gfi wall outlet I installed?

Anyone have ideas?


55gallons is offline   Reply With Quote
Unread 09/23/2008, 01:34 PM   #2
dmo
Registered Member
 
dmo's Avatar
 
Join Date: Dec 2005
Location: Seattle, Wa
Posts: 154
What kind of lighting setup do you have? Is it the breaker popping at the box or the gfci? It may be a better solution to reduce the load on that circuit.


__________________
Daniel

Current Tank Info: 90g reef
dmo is offline   Reply With Quote
Unread 09/23/2008, 01:42 PM   #3
55gallons
Registered Member
 
Join Date: May 2006
Location: Windsor Locks, CT
Posts: 27
Thanks for the response. It's not the GFCI popping. It's the breaker. The thing is I don't want to reduce the load unless I have to....I'm very happy with my setup which includes:

Marineland T5: 2 actinic strips (wattage I can't recall....I'm at work right now), and 2 white strips (wattage can't recall)
and
Coral life unit.. 48" Coralife Aqualight Lunar 4x65watt w/Moon Lights

but it's constantly powering also... mag 5 sump pump, 3 maxijet 1200s, heater, and Tunze skimmer.


55gallons is offline   Reply With Quote
Unread 09/23/2008, 01:53 PM   #4
dmo
Registered Member
 
dmo's Avatar
 
Join Date: Dec 2005
Location: Seattle, Wa
Posts: 154
I don't have any experience with a battery backup, so I can't help there. The load from your tank doesn't seem exceptionally high, do you stagger your lighting so they don't all come on all at the same time? I'm also wondering if maybe there is some condensation getting into the fixture to possibly cause a short on initial startup.. Just a wild guess though.

Hopefully someone with more electrical knowledge will chime in.


__________________
Daniel

Current Tank Info: 90g reef
dmo is offline   Reply With Quote
Unread 09/23/2008, 02:02 PM   #5
55gallons
Registered Member
 
Join Date: May 2006
Location: Windsor Locks, CT
Posts: 27
my lights do alternate. I have a very small corlife light on the sump and another of the same unit on the hang on refugium that turn off at the same time the t5s turn on and blow the breaker


55gallons is offline   Reply With Quote
Unread 09/23/2008, 02:30 PM   #6
BeanAnimal
Registered Member
 
Join Date: Feb 2003
Location: Pittsburgh
Posts: 20,772
Quote:
Originally posted by 55gallons
Thanks for the response. It's not the GFCI popping. It's the breaker. The thing is I don't want to reduce the load unless I have to
YOU HAVE TO REDUCE THE LOAD. You have no choice. The breaker is doing its job and tripping due to an overload.

There is no wiggle room here, you are overloading the circuit long enough for it to trip. Continued tripping is going to weaken the breaker and it will trip sooner.

When ballastss and motors startup they draw many times their rated power. This is called "in-rush current". Breakers do not trip at their EXACT handle rating the exact moment that the rating is exceeded. They can handle short bursts of power that exceed the handle rating.

By code, you should not have a breaker loaded to more than 80% of its rated capacity. This "derating" helps to leave headroom for in-rush current.

Your sysmptoms indicate that you clearly have the circuit overloaded and no longer have enough headroom to accomodate the motors or ballasts starting.



Last edited by BeanAnimal; 09/23/2008 at 02:35 PM.
BeanAnimal is offline   Reply With Quote
Unread 09/23/2008, 02:36 PM   #7
55gallons
Registered Member
 
Join Date: May 2006
Location: Windsor Locks, CT
Posts: 27
But...

Wouldn't a battery backup allow the lights to pull there additional juice during initialization from it rather than the wall


55gallons is offline   Reply With Quote
Unread 09/23/2008, 02:51 PM   #8
BeanAnimal
Registered Member
 
Join Date: Feb 2003
Location: Pittsburgh
Posts: 20,772
In short, no.

The batteries in a UPS are not part of the circuit unless the mains power fails. Even in an "on-line" ups, the batteries are being charged and the DC bus powers the inverter.

You have an overloaded circuit. You need to reduce the load. Either eliminate some items or move then to another circuit.


BeanAnimal is offline   Reply With Quote
Unread 09/23/2008, 03:06 PM   #9
55gallons
Registered Member
 
Join Date: May 2006
Location: Windsor Locks, CT
Posts: 27
Thank you


55gallons is offline   Reply With Quote
Unread 09/23/2008, 03:13 PM   #10
BeanAnimal
Registered Member
 
Join Date: Feb 2003
Location: Pittsburgh
Posts: 20,772
Not a problem my friend

I wish I had more desirable answers for you.


BeanAnimal is offline   Reply With Quote
Unread 09/23/2008, 07:55 PM   #11
J-Burns
Registered Member
 
J-Burns's Avatar
 
Join Date: Jan 2002
Location: Charleston, WV
Posts: 235
You may try replacing the breaker that is tripping. As BeanAnimal said sometimes they get week and start tripping too soon. Get the same size rating that is there now- Probably 15 or 20 amps. You also will need to know who made your box in order to get a breaker that will fit. There is also a possibality that a piece of your equipment is going bad and tripping your breaker. You also may want to get an ammeter to check your current at the breaker 1st to see how many amps you are pulling.


J-Burns is offline   Reply With Quote
Unread 09/23/2008, 08:36 PM   #12
coryjones
Premium Member
 
Join Date: Jul 2007
Location: Decatur
Posts: 489
What about adding capacitors for the start up?


coryjones is offline   Reply With Quote
Unread 09/23/2008, 08:47 PM   #13
A.T.T.R
Registered Member
 
A.T.T.R's Avatar
 
Join Date: Jan 2007
Location: ft lauderdale
Posts: 2,729
caps in AC lines are just filters.
for the most part.

what else is on that breaker.. cause i load mine a heck of alot more then that with no probloms.


__________________
Chris
Addicted to the Reef-

Current Tank Info: Starting a 20g
A.T.T.R is offline   Reply With Quote
Unread 09/23/2008, 08:53 PM   #14
coryjones
Premium Member
 
Join Date: Jul 2007
Location: Decatur
Posts: 489
really because we use them all the time booster cap on ac with hard start compressors and it seems to do the trick. I load my 15amp breaker with 3 400w mh 2 maxi 1200 and fridge with no problems.


coryjones is offline   Reply With Quote
Unread 09/24/2008, 06:17 PM   #15
H20ENG
Pro builder/aquarist hack
 
H20ENG's Avatar
 
Join Date: Jul 2002
Location: NORCAL (Vacaville, CA)
Posts: 5,125
You must be sharing a breaker with the refrigerator, microwave, or similar. Like Bean said, you need to remove some of the load from that breaker- not neccesarily from the tank.

Map out your breakers and outlets. Then see if you can run an extension cord tot he tank so you are splitting the load.

The "hard start" cap will only work on motors, not T5s


H20ENG is offline   Reply With Quote
Unread 09/25/2008, 12:43 PM   #16
coryjones
Premium Member
 
Join Date: Jul 2007
Location: Decatur
Posts: 489
cool didn,t know i know my mh have caps on them.


coryjones is offline   Reply With Quote
Unread 09/25/2008, 01:10 PM   #17
A.T.T.R
Registered Member
 
A.T.T.R's Avatar
 
Join Date: Jan 2007
Location: ft lauderdale
Posts: 2,729
mh only have the caps for power factor correction if i remember correctly?
i think i may be wrong tho where is bean when ya need him


__________________
Chris
Addicted to the Reef-

Current Tank Info: Starting a 20g
A.T.T.R is offline   Reply With Quote
Unread 09/25/2008, 01:24 PM   #18
A.T.T.R
Registered Member
 
A.T.T.R's Avatar
 
Join Date: Jan 2007
Location: ft lauderdale
Posts: 2,729
btw caps on hvacs and fans and.. any motor is to allow a phase shift to start the motor. you ahve more then one winding to provide rotational force untill it starts.


__________________
Chris
Addicted to the Reef-

Current Tank Info: Starting a 20g
A.T.T.R is offline   Reply With Quote
Unread 09/25/2008, 01:31 PM   #19
BeanAnimal
Registered Member
 
Join Date: Feb 2003
Location: Pittsburgh
Posts: 20,772
Quote:
Originally posted by A.T.T.R
mh only have the caps for power factor correction if i remember correctly?
i think i may be wrong tho where is bean when ya need him

As line voltage changes, the lamp current changes. The cap is used to provide a feedback loop to prevent the current changes (it is more complicated than that... but you got the 1 sentace explanation).

The secondary purpose is to make the ballast behave more like a resistive load (a.k.a PF correction).


BeanAnimal is offline   Reply With Quote
Unread 09/25/2008, 01:40 PM   #20
A.T.T.R
Registered Member
 
A.T.T.R's Avatar
 
Join Date: Jan 2007
Location: ft lauderdale
Posts: 2,729
ok well at least i wasnt 100 percent wrong lmao


__________________
Chris
Addicted to the Reef-

Current Tank Info: Starting a 20g
A.T.T.R is offline   Reply With Quote
Unread 09/25/2008, 02:01 PM   #21
8BALL_99
Registered Member
 
8BALL_99's Avatar
 
Join Date: Sep 2004
Location: Toney, AL
Posts: 3,724
I'd see what else is on the circuit.. What you listed isn't enought to overload even a 15amp circuit. I'm not sure what else it could be but you might be lucky enough that there is another circuit by what ever else thats sharing that one with your tank.

Like bean said your only suppose to load them at 80% So even if you get it to stop tripping your so close its still probably over loaded.


__________________
The problem with political jokes is they get elected.

OK, so what's the speed of dark?

Why do we drive on the parkway and park in the driveway?

Isn't is it a bit unnerving that doctors call what they do "practice"?

Current Tank Info: Custom Starfire 300,92Gallon,35 Gallon Hex,Two 40Gallons,125Gallon,
8BALL_99 is offline   Reply With Quote
Unread 09/25/2008, 02:21 PM   #22
coryjones
Premium Member
 
Join Date: Jul 2007
Location: Decatur
Posts: 489
I now enough to do my job but if you had a short which it isn't hard with a tank of salt water and electricity and your breaker trips that breaker needs to be replaced most people reset them but one day i was bored and read info that came with a square d breaker and it says if it trip it needs to be replaced they are made to trip one time and reset until it can be replaced but i know no one does this.


coryjones is offline   Reply With Quote
Unread 09/25/2008, 03:58 PM   #23
REEF-n-Chicago
Registered Member
 
Join Date: Feb 2003
Location: Los Angeles, CA (san pedro)
Posts: 1,456
cory, are you sure this is true? I need to replace a few if so
Cant imagine this is the case though!


__________________
Jordan

My tank gets DRUNK every morning

Current Tank Info: 150 Gallon w/ 100 gallon sump; 240 gallon
REEF-n-Chicago is offline   Reply With Quote
Unread 09/25/2008, 04:24 PM   #24
hellssephiroth
Registered Member
 
hellssephiroth's Avatar
 
Join Date: Mar 2007
Location: Spencer, WI
Posts: 314
i am in no way telling you to do this ..... but i had problems because our apartment we are renting is wired dumber than anything ive seen in my life... living room, kitchen and bedroom are all on one breaker...... wow horrible. it had a 15amp breaker in it and i put in a 30 >< not safe really..... especially if u have older wiring thats why i have good insurance on all my stuff. another option would be to get a seperate breaker like 20 amp and see if u can find what wires go where in your house and put your fishtank on its own seperate breaker? thats what i should do but the landlord told me he would kick me out, should have never mentioned it. another thing is dont have a lot of stuff turn on all at one time take have lights / pumps and w/e else u have regulated turn on a few minutes apart.


hellssephiroth is offline   Reply With Quote
Unread 09/25/2008, 05:05 PM   #25
BeanAnimal
Registered Member
 
Join Date: Feb 2003
Location: Pittsburgh
Posts: 20,772
Quote:
Originally posted by hellssephiroth
it had a 15amp breaker in it and i put in a 30 >< not safe really.....
That is an understatement. It is irresponsible, negligent and stupid. You lived in an apartment, you overloaded a circuit and THEN disabled the fire protection for the circuit. If you caused a fire and killed people you would be 100% responsible.

Quote:
another option
YOU may think that it is an option but it is not. Oversizing a breaker could/should land you in jail. In your own house, your own family... take it up with them. Then again what about the firefighters that put their lives on the line to save you and your family because you decided a 30A breaker was ok to use in place of a 15A breaker.

Worse, it was not YOUR own home, it was an apartment and other peoples families, shame on you for doing it, and offering it as an option to other people.

Quote:
thats what i should do but the landlord told me he would kick me out
To be 100% truthful, your landlord should kick you out. If I can find his/her name I will certainly speed up that process.

Breakers are sized by code and wire size for a reason. If you are tripping the breaker, then upsizing it to your whim is not an option. It is not safe and it is not legal. It is an act of negligence and ignorance is not an excuse.

So you say "I am in no way telling you to do this..." and then give people advice that you KNOW is bad and/or deadly as an "option" and somehow think it is ok?

If I sound harsh it is because this is a very serious subject.



Last edited by BeanAnimal; 09/25/2008 at 05:17 PM.
BeanAnimal is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On



All times are GMT -6. The time now is 11:04 AM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
Powered by Searchlight © 2025 Axivo Inc.
Use of this web site is subject to the terms and conditions described in the user agreement.
Reef CentralTM Reef Central, LLC. Copyright ©1999-2022
User Alert System provided by Advanced User Tagging v3.3.0 (Pro) - vBulletin Mods & Addons Copyright © 2025 DragonByte Technologies Ltd.