Unfinished basement, adding outlets and circuits etc

Morning everyone, I have plans to add electrical outlets to my basement which is my fish tank room. I want advice as to what would be optimal. If you were to redo your tank room (3+ tanks fw and sw) how would you have the electrical set up? Two 20a Circuits? I'm not an electrical guy but the person who is going to help me do it will know what I'm saying if I tell him what I want.


PAXpress is offline   Reply With Quote
Unread 05/18/2016, 09:45 AM   #2
yacn
Registered Member
 
Join Date: Nov 2007
Location: Detroit, Michigan
Posts: 212
I have one 20 amp circuit I installed in my basement to run my sump equipment.

I've never tripped the breaker. At one time I had all these running at one time on this circuit (Dolphin 4000/3000 return pump, (2) 200 watt heaters, CFL 40 watt fuge light, 25 watt UV sterilizer, Marineland Magnum 350, air pump, skimmer w/ Sedra 3500 pump, and several power heads to run ATO, GFO, UV, etc. Plus I would run 2 more 100 watt heaters and Rio 1100 pump when doing water changes....had (2) garbage cans with salt water. Some of the equipment listed would be unplugged during water changes.

My MH/VHO lights were set up on another circuit on 1st floor where DT is located.....1080 watts.

Looks like you may need (2) 20 amp circuits for your needs.

I also used larger gauge wire for the 20 amp circuit....which your friend should know.


yacn is offline   Reply With Quote
Unread 05/18/2016, 09:57 AM   #3
PAXpress
Registered Member
 
Join Date: Nov 2015
Posts: 312
Quote:
Originally Posted by yacn View Post
I have one 20 amp circuit I installed in my basement to run my sump equipment.

I've never tripped the breaker. At one time I had all these running at one time on this circuit (Dolphin 4000/3000 return pump, (2) 200 watt heaters, CFL 40 watt fuge light, 25 watt UV sterilizer, Marineland Magnum 350, air pump, skimmer w/ Sedra 3500 pump, and several power heads to run ATO, GFO, UV, etc. Plus I would run 2 more 100 watt heaters and Rio 1100 pump when doing water changes....had (2) garbage cans with salt water. Some of the equipment listed would be unplugged during water changes.

My MH/VHO lights were set up on another circuit on 1st floor where DT is located.....1080 watts.

Looks like you may need (2) 20 amp circuits for your needs.

I also used larger gauge wire for the 20 amp circuit....which your friend should know.
Well he was asking if I would need a 40 amp circuit. I'm sure he knows about the larger gauge.


PAXpress is offline   Reply With Quote
Unread 05/18/2016, 09:58 AM   #4
moatdaddy
Registered Member
 
moatdaddy's Avatar
 
Join Date: Mar 2006
Location: Panama City beach florida
Posts: 848




lol look at my electrical cords. it is ugly, i had two installed less than a week ago. I did two out of fear of tripping, did 20 amp breakers. He measured the amps coming through one was 5.6 and the other was 1.4. so i could have gone with just one, but meh. It cost me 170 to get one done, 200 to get a second done, so for 30 bucks i could get a little more done. in the end the electrician coming out has a cost as does his time.


moatdaddy is offline   Reply With Quote
Unread 05/18/2016, 09:58 AM   #5
yacn
Registered Member
 
Join Date: Nov 2007
Location: Detroit, Michigan
Posts: 212
I would go with (2) 20 amp circuits


yacn is offline   Reply With Quote
Unread 05/18/2016, 10:27 AM   #6
PAXpress
Registered Member
 
Join Date: Nov 2015
Posts: 312
Luckily I will only need to pay for the parts as he owes me a favor and will do all the work without charge (I'll sweeten the deal with a thank you gift card or buy him lunch or something sometime). 2 20amp and should I have a seperate circuit for the rest of the basement (in case I decide to finish it)?


PAXpress is offline   Reply With Quote
Unread 05/18/2016, 10:29 AM   #7
PAXpress
Registered Member
 
Join Date: Nov 2015
Posts: 312
Quote:
Originally Posted by moatdaddy View Post




lol look at my electrical cords. it is ugly, i had two installed less than a week ago. I did two out of fear of tripping, did 20 amp breakers. He measured the amps coming through one was 5.6 and the other was 1.4. so i could have gone with just one, but meh. It cost me 170 to get one done, 200 to get a second done, so for 30 bucks i could get a little more done. in the end the electrician coming out has a cost as does his time.
Whew! Thats looking pretty intricate! Pretty sure my wife would strangle me if she saw that type of situation in my basement! HAHA Next project will be a work bench in the basement with storage shelving.


PAXpress is offline   Reply With Quote
Unread 05/18/2016, 11:01 AM   #8
FirstContact
Registered Member
 
FirstContact's Avatar
 
Join Date: Jan 2006
Location: Glenn Dale, MD
Posts: 1,613
Have two 20 amp circuits in the basement. Check out the electrical articles on BeanAnimals website for how to do the circuits and outlets!

http://www.beananimal.com/articles/e...he-reefer.aspx


__________________
No man is an island entire of itself; any man's death diminishes me, because I am involved in mankind; never send to know for whom the bell tolls; it tolls for thee.
John Donne

Current Tank Info: 120g Reef 100g Rubbermaid Sump, 20g Refugium; previous tank: 46g Drilled; Self Plumbed, Birds Nest, Anchor, Xenia, Zoas, Yuma Yuma Ricordea, Chalice, Mushrooms, Brain, Acan, Anenome Plate; Clams, Other Inverts, Fish, Live Rock
FirstContact is offline   Reply With Quote
Unread 05/18/2016, 11:59 AM   #9
PAXpress
Registered Member
 
Join Date: Nov 2015
Posts: 312
Quote:
Originally Posted by FirstContact View Post
Have two 20 amp circuits in the basement. Check out the electrical articles on BeanAnimals website for how to do the circuits and outlets!

http://www.beananimal.com/articles/e...he-reefer.aspx
Lots of info there. Read through a bit of it. I'll refer to that if I run into issues or questions.


PAXpress is offline   Reply With Quote
Unread 05/18/2016, 02:36 PM   #10
billdogg
Registered Member
 
billdogg's Avatar
 
Join Date: Apr 2008
Location: Grove City, Ohio
Posts: 10,806
Although it was overkill, I ran 2 x 20A circuits to my fish room, with GFCI outlets. I figured that the cost to run 2 was only slightly more than one, and since I was doing the work myself, labor didn't cost me anything. I like the ability to split various items between the two circuits so that if one trips, the other can keep the tank going.

You MUST use 12/2 wire and 20A receptacles or you run the risk of overheating the wire and causing a fire. Unlikely with the loads we typically use, but the proper way to do it nonetheless.


__________________
I'll try to be nice if you try to be smarter!
I can't help that I grow older, but you can't make me grow up!

Current Tank Info: 120 mixed reef with 40b sump, RO 150 skimmer, AI Sol Blue x 2, and a 60g Frag Tank with 100g rubbermaid sump. 2 x Kessil A360w lights, BM curve 5 skimmer
billdogg is offline   Reply With Quote
Unread 05/18/2016, 10:30 PM   #11
jason2459
Registered Member
 
jason2459's Avatar
 
Join Date: Jul 2009
Location: Iowa
Posts: 9,671
I've got 4 individual 20amp gfci circuits. 2 upstairs for the display tank split up between left and right side tank equipment.

Then 2 for the basement sump area. All using 12/2 plus ground like mentioned above.


__________________
rebuild and recovery log:
No more red house, you'll have to click on my name and visit my homepage!

You can check out my parameters at reeftronics dot net website and look for my username.

Current Tank Info: 180g mixed reef w/ a beananimal overflow to a dolomite RRUGF. | 20g long G. Smithii Mantis Tank
jason2459 is offline   Reply With Quote
Unread 05/19/2016, 05:15 AM   #12
mcgyvr
Registered Member
 
mcgyvr's Avatar
 
Join Date: Sep 2003
Location: North Carolina
Posts: 20,050
You didn't state what equipment you will have so we cannot recommend how many circuits you need...


__________________
Who me?
mcgyvr is offline   Reply With Quote
Unread 05/19/2016, 06:05 AM   #13
jason2459
Registered Member
 
jason2459's Avatar
 
Join Date: Jul 2009
Location: Iowa
Posts: 9,671
Quote:
Originally Posted by mcgyvr View Post
You didn't state what equipment you will have so we cannot recommend how many circuits you need...
I would always recommend a minimum of two separate gfci or afci/gfci circuits. Spread equipment across both so there's some kind of life support on both incase one pops.


__________________
rebuild and recovery log:
No more red house, you'll have to click on my name and visit my homepage!

You can check out my parameters at reeftronics dot net website and look for my username.

Current Tank Info: 180g mixed reef w/ a beananimal overflow to a dolomite RRUGF. | 20g long G. Smithii Mantis Tank
jason2459 is offline   Reply With Quote
Unread 05/19/2016, 11:48 AM   #14
JB NY
Registered Member
 
JB NY's Avatar
 
Join Date: Mar 2001
Location: Long Island, NY
Posts: 9,207
When I put in a dedicated sump room in my basement I put in two dedicated 20amp circuits. 10 years later I still don't need anymore power.


__________________
-Joe

TOTM Sept 2002 | Reefland April 2004 | CORAL Magazine Nov 2007
Featured Tank "Coral Reef Aquarium" 2011 | Reef Spotlight 2018

Current Tank Info: 270G SPS Tank, 140G sumps, 35G Frag Tank, Ultra Reef Akula UKS-200 Skimmer, Apex, Giesemann Spectra 3x250W MH 4x80W T5, 2xReefbrite Tech 72" Blue LED, Triton Dosing, ARID C30 Algae Reactor, Maxspect Gyre
JB NY is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On



All times are GMT -6. The time now is 02:44 PM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
Powered by Searchlight © 2025 Axivo Inc.
Use of this web site is subject to the terms and conditions described in the user agreement.
Reef CentralTM Reef Central, LLC. Copyright ©1999-2022
User Alert System provided by Advanced User Tagging v3.3.0 (Pro) - vBulletin Mods & Addons Copyright © 2025 DragonByte Technologies Ltd.