Electrical Upgrade Advice Needed

The school has electricians there this week and has agreed to upgrade the electrical for the fish tank. What should I ask for???

The outlet is T'ed off another outlet which has 2 computers and printers plugged in which I don't want to fry! On my outlet I have 2x 4bulb Compact fluorescents with balasts, 2 powerheads, a canister filter, 2 heaters and a pump, plus I want to add a sump with lighting and a skimmer. I have no idea how much amperage this is all drawing, but assuming I can ask for anything...what would you ask for? Plus should all my outlets be in the cabinet where the sump will be or behind the tank which is not very accessible but IS away from so much water.

Thanks for all your advice!!!


gwenvet is offline   Reply With Quote
Unread 11/20/2008, 01:47 PM   #2
Michael
NTTH Rookie Help
 
Michael's Avatar
 
Join Date: Jan 2008
Location: Gloucester, England,UK
Posts: 7,808
Blog Entries: 6
the electricians will know what to do, you wont need to worry there


__________________
Don't be afraid to ask questions, we in the new to the hobby are here to help you
[For My Tank Spec,Photo Album,Articles and website, click on my name]

MY Very Kindest and Warmest Regards ,
MIKE

Current Tank Info: I have a 92 gal Corner Tank, and way too many pieces of equipment to list really, (proud member of the reef central corner club)
Michael is offline   Reply With Quote
Unread 11/20/2008, 01:49 PM   #3
qfrisco
Registered Member
 
Join Date: Dec 2007
Location: Dallas, TX Area
Posts: 1,389
At the very least have them run one dedicated 20-amp circuitfrom the breaker to your tank. If they're using standard wiring, the same bundle of wiring should support a second line, so go ahead and have them wired to separate receptacles (so two new breakers at the circuit breaker, wired to outlets by the tank.) Also, go ahead and have them install GFCI outlets.

You can split your pumps across the two lines so you'll still get some circulation in the event one of the circuits trips.


qfrisco is offline   Reply With Quote
Unread 11/20/2008, 02:03 PM   #4
kevin2000
Registered Member
 
Join Date: Jan 2004
Location: Portland, Oregon
Posts: 3,805
My 02

Depends on what your long term plans are.

Every tank should be connected to a GFI receptacle - mandatory to help keep you and your student from getting fried. If you don't have one now you need to have one installed (no big deal and easy to do).

I get the impression you have a std tank without much of an electrical demand ... if so you don't need a dedicated line. However if you are considering a MAJOR upgrade down the line which would significantly increase your electric demand you might ask for for a dedicated line.

Regardless of electric demand - its always nice to have one or two electrical boxes installed in the cabinet under the tank - gives you flexibility and helps keep things neater with less wires running out of the cabinet.

Good luck.


kevin2000 is offline   Reply With Quote
Unread 11/20/2008, 02:03 PM   #5
gwenvet
Premium Member
 
gwenvet's Avatar
 
Join Date: Nov 2008
Location: West Lafayette, Indiana
Posts: 300
So one new circuit with two breakers leading to two GFCI outlets behind the tank, and then two power strips (one from each outlet) leading under the tank where the sump will be?

Kevin: I was thinking 10 things plugged into one outlet was a lot, but I'm a newbie and have no idea how much a lot is! If we did eventually go to metal halide lights and a reef tank, with Ca reactors and the like, would we need a dedicated line then?


gwenvet is offline   Reply With Quote
Unread 11/20/2008, 02:08 PM   #6
Jerm77
Registered Member
 
Jerm77's Avatar
 
Join Date: Nov 2008
Location: NORCAL
Posts: 499
you can add up all the wattage on all the devices you are going to run then divide by 120 this will give you your Amp requirements. or you can add up the amps used by all the devices. you can safely run 80% to a circuit.

so if its a 20amp circuit you can run up to 16amps.

the electricians should be able to determine if the sub panel or main can handle the extra load if any.

just an example:

400watts / 120(volts) = 3.33 amps. 20 amps should be able to handle most mediums sized aquariums.



Last edited by Jerm77; 11/20/2008 at 02:16 PM.
Jerm77 is offline   Reply With Quote
Unread 11/20/2008, 02:13 PM   #7
qfrisco
Registered Member
 
Join Date: Dec 2007
Location: Dallas, TX Area
Posts: 1,389
Quote:
Originally posted by gwenvet
So one new circuit with two breakers leading to two GFCI outlets behind the tank, and then two power strips (one from each outlet) leading under the tank where the sump will be?

Kevin: I was thinking 10 things plugged into one outlet was a lot, but I'm a newbie and have no idea how much a lot is! If we did eventually go to metal halide lights and a reef tank, with Ca reactors and the like, would we need a dedicated line then?
If you're referring to my suggestion, it would be two circuits with one breaker each, with each circuit leading to a GFCI outlet. You then go from the outlets to power strips as necessary.

For several months, I ran 2x250w metal halides, plus your standard list of pumps and powerheads on a circuit that was shared with my fridge and microwave, and the breaker didn't trip a single time. You can support quite a few things with one 20 amp circuit, but if you can get it, dedicated lines would be even better.


qfrisco is offline   Reply With Quote
Unread 11/20/2008, 02:34 PM   #8
kevin2000
Registered Member
 
Join Date: Jan 2004
Location: Portland, Oregon
Posts: 3,805
Quote:
Originally posted by gwenvet
So one new circuit with two breakers leading to two GFCI outlets behind the tank, and then two power strips (one from each outlet) leading under the tank where the sump will be?

Kevin: I was thinking 10 things plugged into one outlet was a lot, but I'm a newbie and have no idea how much a lot is! If we did eventually go to metal halide lights and a reef tank, with Ca reactors and the like, would we need a dedicated line then?
Many and perhaps most "reefers" don't have dedicated lines to their fish tanks - even with MH lights. However - there comes a time when demands on that line get so high that it requires it.

The number of connections isn't always a good judge of the "load" on the line (know that I am not an electrician and am using common sense/experience rather than real "know how"). Its pretty common for tanks to have multiple connections just for the power heads alone .. then you need to add heater, skimmer, lights etc. - whether thats too much for the circuit depends on the circuit and what else is on it.

When in doubt ... before the electricians come out use "google" and come up with your "shopping list" and then print out the info on the lighting, cooling etc that you may want in the future and provide that info to the electrician when he arrives.


kevin2000 is offline   Reply With Quote
Unread 11/20/2008, 03:00 PM   #9
Jerm77
Registered Member
 
Jerm77's Avatar
 
Join Date: Nov 2008
Location: NORCAL
Posts: 499
Quote:
Originally posted by gwenvet
I was thinking 10 things plugged into one outlet was a lot
its not the amount of things plugged to worry about. its about how many amps each plug can handle. most sockets are rated for 15 amps. most power strips are rated for the same or less. just look at the sticker on the power strip.


Jerm77 is offline   Reply With Quote
Unread 11/20/2008, 04:30 PM   #10
gwenvet
Premium Member
 
gwenvet's Avatar
 
Join Date: Nov 2008
Location: West Lafayette, Indiana
Posts: 300
Thanks for all the suggestions. I will try for a dedicated circuit with GFCI and will see where that gets me.
Do people with sumps still keep powerstrips under the tank with the sump or is that asking for trouble?


gwenvet is offline   Reply With Quote
Unread 11/20/2008, 04:41 PM   #11
Jerm77
Registered Member
 
Jerm77's Avatar
 
Join Date: Nov 2008
Location: NORCAL
Posts: 499
i would keep all electricity away from the water. if it needs to be in the cabinet, make sure its secure and away from moisture with no chance of water spilling or overflowing onto the electrical.


Jerm77 is offline   Reply With Quote
Unread 11/20/2008, 04:54 PM   #12
kevin2000
Registered Member
 
Join Date: Jan 2004
Location: Portland, Oregon
Posts: 3,805
Water and electriciy don't mix well ... how much of a problem you may have depends on how large the cabinet is and your particular setup - add some curious school kids and its get even more complicated.

RC should have plenty of pics on-line of tank setups along with their sumps/electrical hookups - those pics may give you some idea of what people are doing.


kevin2000 is offline   Reply With Quote
Unread 11/20/2008, 04:58 PM   #13
qfrisco
Registered Member
 
Join Date: Dec 2007
Location: Dallas, TX Area
Posts: 1,389
Quote:
Originally posted by gwenvet
Thanks for all the suggestions. I will try for a dedicated circuit with GFCI and will see where that gets me.
Do people with sumps still keep powerstrips under the tank with the sump or is that asking for trouble?
I have three powerstrips in the cabinet under my 90g, sharing the space with my sump and top-off reservoir. I do have them mounted up high and anything that's plugged in has a drip loop.


qfrisco is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On



All times are GMT -6. The time now is 01:15 PM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
Powered by Searchlight © 2025 Axivo Inc.
Use of this web site is subject to the terms and conditions described in the user agreement.
Reef CentralTM Reef Central, LLC. Copyright ©1999-2022
User Alert System provided by Advanced User Tagging v3.3.0 (Pro) - vBulletin Mods & Addons Copyright © 2025 DragonByte Technologies Ltd.