Question GFCI tripped!

...this evening and I'm glad I noticed it because of course my filter and heater were not on. What in the heck would have caused it to trip?!


__________________
29 cube
Jlobo is offline   Reply With Quote
Unread 05/03/2011, 10:57 PM   #2
PMUnprotected
Registered Member
 
Join Date: Jan 2011
Posts: 146
Could be a bad pump or powerhead if you have them. Mine tripped bc my pump had a short.


__________________
55g column style, 10g sump/refugium, 40 lbs LS, 40+ lbs LR, AI Sol Blue, Midas Blenny, Tomato Clownfish, peppermint shrimp, astrea snails, cerith snails, nessarious snails, dwarf hermits
PMUnprotected is offline   Reply With Quote
Unread 05/03/2011, 11:05 PM   #3
disc1
-RT * ln(k)
 
disc1's Avatar
 
Join Date: Sep 2010
Location: Little Rock
Posts: 9,705
Reset it. If it trips again, start unplugging one thing at a time until you figure out what's tripping it.


disc1 is offline   Reply With Quote
Unread 05/04/2011, 08:41 AM   #4
Vinny Kreyling
Registered Member
 
Vinny Kreyling's Avatar
 
Join Date: Nov 2002
Location: Miller Place, NY
Posts: 7,206
I had a bad heater trip mine.


Vinny Kreyling is offline   Reply With Quote
Unread 05/04/2011, 09:14 AM   #5
roli112
Registered Member
 
roli112's Avatar
 
Join Date: Apr 2011
Location: Los Angeles
Posts: 298
More times than anything it would be a bad heater


__________________
180 gallon mixed reef

Current Tank Info: 180g. mix reef
roli112 is offline   Reply With Quote
Unread 05/04/2011, 09:51 AM   #6
computeaholic
Registered Member
 
Join Date: Nov 2009
Location: Oklahoma City, OK
Posts: 76
+1 for the heater. Usually need to replace once a year.


computeaholic is offline   Reply With Quote
Unread 05/04/2011, 09:57 AM   #7
bluebill
Registered Member
 
Join Date: Sep 2010
Location: Birmingham, AL
Posts: 66
It could be anything. Including to many things "comming on" at the same time. GFCI's are designed to detect a sudden changes in current and trip. I would not be concerned unless it continues then start with the heater like the other posters have said. Also if the GFCI has tripped alot you may want to replace it also, because like a breaker they are consider no good once the trip (due to its ability to read current accurately over time/contacts become weak).


bluebill is offline   Reply With Quote
Unread 05/04/2011, 10:01 AM   #8
Jlobo
Registered Member
 
Jlobo's Avatar
 
Join Date: Jan 2011
Location: Lewiston, Idaho
Posts: 359
Well I hope it's not my 3 week old Jager heater! My fear is that it will trip when I'm sleeping at night and that I will wake up to some very oxygen starved and cold critters.


__________________
29 cube
Jlobo is offline   Reply With Quote
Unread 05/04/2011, 10:06 AM   #9
MalHavoc
Infinitely Prolonged
 
Join Date: Apr 2002
Location: Canada
Posts: 10,850
Quote:
Originally Posted by bluebill View Post
GFCI's are designed to detect a sudden changes in current and trip.
No, not quite. They detect the difference between the current flowing into a circuit and the current flowing back out of it. The idea is that the device that is causing a problem has become grounded some how, and current is flowing to ground instead of going back through the GFCI.


__________________
Jason

"Empathy, he once had decided, must be limited to herbivores or anyhow omnivores who could depart from a meat diet. Because, ultimately, the empathic gift blurred the boundaries between hunter and victim, between the successful and the defeated."

-- Do Androids Dream of Electric Sheep?, Philip K Dick
MalHavoc is offline   Reply With Quote
Unread 05/04/2011, 10:13 AM   #10
bluebill
Registered Member
 
Join Date: Sep 2010
Location: Birmingham, AL
Posts: 66
I do agree. But a circuit being ground is not the only thing. This would continue the GFCI to trip. Sudden changes I mean are more like a spike for example you have a chest freezer in your garage, and while you are cutting wood (from a protected outlet), the compressor to the freezer kicks on at the same time and it trips. But with this it could go on forever.


bluebill is offline   Reply With Quote
Unread 05/04/2011, 10:46 AM   #11
snorvich
Team RC member
 
snorvich's Avatar
 
Join Date: Aug 2005
Location: Outlander
Posts: 40,953
Blog Entries: 46
Quote:
Originally Posted by MalHavoc View Post
No, not quite. They detect the difference between the current flowing into a circuit and the current flowing back out of it. The idea is that the device that is causing a problem has become grounded some how, and current is flowing to ground instead of going back through the GFCI.
Yes, I agree. Some devices such as heaters or chillers require a fairly large amount of amps when they start up. Most plugs have either 15 or 20 amps maximum before they trip the GFCI. I always try to load balance because I have a lot of stuff on my tank and that is not even counting lights which are on separate circuits.


__________________
Warmest regards,
~Steve~
snorvich is offline   Reply With Quote
Unread 05/04/2011, 10:54 AM   #12
MalHavoc
Infinitely Prolonged
 
Join Date: Apr 2002
Location: Canada
Posts: 10,850
Yeah. a GFCI will *not* trip because of a load surge when a device is turned on. A panel breaker may trip because of a surge if the surge hits the max rated value for the breaker, but a GFCI compares current in the hot versus neutral, which should only be different if there is a short to ground.


__________________
Jason

"Empathy, he once had decided, must be limited to herbivores or anyhow omnivores who could depart from a meat diet. Because, ultimately, the empathic gift blurred the boundaries between hunter and victim, between the successful and the defeated."

-- Do Androids Dream of Electric Sheep?, Philip K Dick
MalHavoc is offline   Reply With Quote
Unread 05/05/2011, 09:23 AM   #13
RocketSurgeon
Registered Member
 
Join Date: Jul 2010
Location: Houston, Texas
Posts: 653
Quote:
Originally Posted by malhavoc View Post
yeah. A gfci will *not* trip because of a load surge when a device is turned on. A panel breaker may trip because of a surge if the surge hits the max rated value for the breaker, but a gfci compares current in the hot versus neutral, which should only be different if there is a short to ground.

+1


RocketSurgeon is offline   Reply With Quote
Unread 05/06/2011, 07:33 AM   #14
RocketSurgeon
Registered Member
 
Join Date: Jul 2010
Location: Houston, Texas
Posts: 653
Quote:
Originally Posted by Jlobo View Post
...this evening and I'm glad I noticed it because of course my filter and heater were not on....
what's the verdict? did you reset it, and everything back to normal? or was there something a miss?


RocketSurgeon is offline   Reply With Quote
Unread 05/06/2011, 08:29 AM   #15
Jlobo
Registered Member
 
Jlobo's Avatar
 
Join Date: Jan 2011
Location: Lewiston, Idaho
Posts: 359
Yeah, just reset it and things have been working fine. I really want to rule out my brand new Jager heater so I'm wondering if I could have something to do with my cheap Marineland light timer??? I removed that. So far, so good.


__________________
29 cube
Jlobo is offline   Reply With Quote
Unread 05/06/2011, 08:36 AM   #16
RocketSurgeon
Registered Member
 
Join Date: Jul 2010
Location: Houston, Texas
Posts: 653
Keep in mind that GFCI outlets do go bad. They will begin to trip more easily more often.


RocketSurgeon is offline   Reply With Quote
Unread 05/06/2011, 10:29 AM   #17
Jlobo
Registered Member
 
Jlobo's Avatar
 
Join Date: Jan 2011
Location: Lewiston, Idaho
Posts: 359
ok, I will. I've only had the thing for about 2 months. Maybe it's just a piece of junk and I should just plug everything back into the wall outlet for now??


__________________
29 cube
Jlobo is offline   Reply With Quote
Unread 05/06/2011, 10:33 AM   #18
RocketSurgeon
Registered Member
 
Join Date: Jul 2010
Location: Houston, Texas
Posts: 653
NEGATIVE. I don't ever recommend having electricity and water together without a GFCI.


RocketSurgeon is offline   Reply With Quote
Unread 05/06/2011, 10:45 AM   #19
ryeguyy84
Registered Member
 
ryeguyy84's Avatar
 
Join Date: Mar 2011
Location: New Jersey
Posts: 2,753
Quote:
Originally Posted by RocketSurgeon View Post
NEGATIVE. I don't ever recommend having electricity and water together without a GFCI.
you should see when a refugium light falls in , that thing tripped real fast. all the fish survived BTW


ryeguyy84 is offline   Reply With Quote
Unread 05/06/2011, 09:42 PM   #20
Jlobo
Registered Member
 
Jlobo's Avatar
 
Join Date: Jan 2011
Location: Lewiston, Idaho
Posts: 359
okay, okay, I'll leave it plugged in.


__________________
29 cube
Jlobo is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Chiller tripping GFCI issue mikeintosh Lighting, Filtration & Other Equipment 10 09/22/2011 10:40 AM
UPS and GFCI - recommendations please pompeyjohn New to the Hobby 9 05/10/2010 04:30 PM


All times are GMT -6. The time now is 01:13 AM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
Powered by Searchlight © 2025 Axivo Inc.
Use of this web site is subject to the terms and conditions described in the user agreement.
Reef CentralTM Reef Central, LLC. Copyright ©1999-2022
User Alert System provided by Advanced User Tagging v3.3.0 (Pro) - vBulletin Mods & Addons Copyright © 2025 DragonByte Technologies Ltd.