12/03/2015, 12:22 PM | #1 |
Registered Member
Join Date: Jan 2015
Posts: 1,598
|
Portable generator and wattage recomendation
I am shopping for a portable power generator. It will be used for the tank only. It will be stored in the garage and moved outside when operated.
I have two dedicated circuits: Circuit #1 (has all the essentials) one return pump one gyre one heater 800w one light one skimmer one ATO pump one doser recator pump (gfo/carbon) Circuit #2 One return pump one heater 800w one light UV pump UV lamp fuge light circulation fan From MyApex, I have a peak of 12 amps on 2 power bars. One heater doesn't kick in at all. I am thinking, if I have power outage and the HVAC is not working, the second heater will kick in and brings the total amperage higher. How big of a generator I need to buy? Any recommendation on brands? I am considering 1700W and 2500W by PowerBoss. http://www.powerboss-equipment.com/p...f95b02a27538d7 http://www.powerboss-equipment.com/p...2942c1525807c1
__________________
325G DT. 100G sump. In-sump refugium. SRO-5000SSS. 2 Gyres 150. 2 Water Blaster HY-5000. 2 Razor 320W. Apex Gold. MR2 GFO. 2 800W Heaters. Tunze Osmolater. 2 20g-long QT tanks. Geo 624 CA. 80W UV |
12/03/2015, 12:27 PM | #2 |
Registered Member
Join Date: Jul 2005
Location: North Texas
Posts: 605
|
No clue on the power usage part but one day I plan to get the generator below. I really want one that will run on gas or propane.
http://www.costco.com/Champion-7000W...100220385.html |
12/03/2015, 12:29 PM | #3 |
Registered Member
Join Date: Feb 2006
Location: at the Beach in Fl
Posts: 792
|
both would theoretically work. I would suggest getting a minimum of 3500 running watts generator. You are always going to want to plug in more than the tank when the power is out. Plus most generators run much more efficiently when only at a half load versus an almost full load.
__________________
"Aliie, Eat a Snickers, you're "HANGRY" - me "I sometimes enjoy watching shadow puppet shows" - jpfelix "Bacon is Love." - Fat Man Current Tank Info: 240 Algae Farm System Running |
12/03/2015, 12:34 PM | #4 |
Registered Member
Join Date: Jan 2015
Posts: 1,598
|
Bigger is better, of course. But, the reasons I don't want large one is storage space and weight. I am really tight on garage space, and I am worried about the weight. The 2500W is more than 100lbs. It is not a problem for me, but I am considering when I am away and someone is looking after my tank. I want the procedure to be easy and painless.
__________________
325G DT. 100G sump. In-sump refugium. SRO-5000SSS. 2 Gyres 150. 2 Water Blaster HY-5000. 2 Razor 320W. Apex Gold. MR2 GFO. 2 800W Heaters. Tunze Osmolater. 2 20g-long QT tanks. Geo 624 CA. 80W UV |
12/03/2015, 12:39 PM | #5 |
Registered Member
Join Date: Dec 2014
Location: Downingtown, PA
Posts: 4,017
|
A lot of the larger gennies come on wheels or you can buy a wheel kit for them. You also want one that has a built in invertor so that the power is smooth and not all over the place which is bad for electronics. Finally if you are worried about someone else needing to start it get one with electric start.
__________________
150 SC tank build: http://www.reefcentral.com/forums/showthread.php?t=2550948 Some have bar tabs. I have a coral tab at my LFS. Life goals. |
12/03/2015, 01:09 PM | #6 |
Registered Member
Join Date: Feb 2006
Location: at the Beach in Fl
Posts: 792
|
my 3500 is on a 2 wheel cart. its not much if any bigger than the ones you have listed.
__________________
"Aliie, Eat a Snickers, you're "HANGRY" - me "I sometimes enjoy watching shadow puppet shows" - jpfelix "Bacon is Love." - Fat Man Current Tank Info: 240 Algae Farm System Running |
12/03/2015, 03:35 PM | #7 |
Registered Member
Join Date: Feb 2013
Location: Maryland
Posts: 3,121
|
Honda simply can't be beat for quality, simplicity and reliability. They always seem to start even after less than perfect maintenance & a long time in storage. You would want an inverted generator or your DC pumps, LED fixture & Alex could be at risk.
You didn't list the wattages for all of your equipment, but 1700w won't be enough if both heaters are needed. You don't mention where you live & what type of ambient room temperature is possible in a worse case scenario. Even a 2500w could be cutting it close if you had the lights on plus a few other things. A tank sitter may need to be trained in what non critical items might need to be shut off during use of the genset. I'd go 3000w just for the extra capacity and the ability to possibly run some other things like a refrigerator, TV, etc. |
12/03/2015, 03:49 PM | #8 | |
Registered Member
Join Date: Dec 2014
Location: Downingtown, PA
Posts: 4,017
|
Quote:
I have a larger rigid brand for my house but ONLY bought it because it was made by Yamaha with a Yamaha engine in it then slapped with a rigid sticker on it and sent out the door. My smaller race genny is a honda though simply since I got a great deal on a used one.
__________________
150 SC tank build: http://www.reefcentral.com/forums/showthread.php?t=2550948 Some have bar tabs. I have a coral tab at my LFS. Life goals. |
|
12/03/2015, 04:09 PM | #9 |
Registered Member
Join Date: Apr 2014
Posts: 333
|
I got a 3100W Champion with built in inverter after we lost power for 48hrs and I decided I didn't want to go through that again. It was pretty cheap at Cabelas and got good reviews. Reading your thread I just realized it's probably been almost 6 months since I started it and I just went out and started it on the first pull.
|
12/03/2015, 05:40 PM | #10 |
Registered Member
Join Date: Dec 2014
Location: somewhere in the midwest
Posts: 227
|
I got my self a 5000w Gen from champion with electric start, It can run the entire house and tank. I out it on a two wheel dolly.
|
12/03/2015, 06:36 PM | #11 |
Registered Member
Join Date: Feb 2003
Location: Pittsburgh
Posts: 20,772
|
You folks with the "discount" gensets: You can't go by the nameplate rating, by a longshot. You can get a rough idea by the engine horsepower, but only rough.
1 Horsepower = 745.7 Watts So if you take that 1 horsepower output from the motor and dump it into the generator shaft, the generator puts out something less than 745.7 Watts due to mechanical and electromechanical losses. The discount Asian units may be as low as 50% efficient, the more expensive high end units may be north of 80% efficient. Lets do some math: 5 Horsepower engine = 3728.5 Watts Output between ~1865 - 3170 Watts. 10 Horsepower engine 7457 Watts Output between ~3300 - 6350 Watts Some of the vendors of the Asian stuff are actually fairly honest. The champion, harbor freight and some others have nameplate ratings that are believable. That said, you really need to be careful when buying a generator. Honda engines are very reliable. The Asian knock-offs... hit or miss. I (personally) would avoid the Briggs/Tecumseh, etc. A Honda engine on a cheap genset is better than a knock-off on a cheap genset. The Honda branded generators are top notch, but VERY expensive. If you ARE NOT mechanical and expect to get a fair amount of use out of your genset, then buy the Honda. On the other hand, if you don't mind working on small engines or don't expect much use, then get the cheaper stuff. If it does not get regular use, then you MUST drain the fuel and clean out the carb, otherwise it WILL get gummed up/varnished sitting for extended periods. Fuel additive only goes so far. |
12/03/2015, 07:59 PM | #13 |
Registered Member
Join Date: Feb 2003
Location: Pittsburgh
Posts: 20,772
|
I have seen quite a few of those around lately. I almost grabbed one myself
|
12/03/2015, 08:06 PM | #14 |
RC Mod
|
That one's 80kw. Gave my old 75kw to the fire hall across the street. The old ones can be had for a song. Parts are getting hard to find.
__________________
Jesse I'm not saying I'm Batman. I'm just saying nobody has ever seen me and Batman in a room together. |
12/03/2015, 08:10 PM | #15 |
Registered Member
Join Date: Jun 2011
Posts: 820
|
Get LL
|
12/03/2015, 08:13 PM | #16 |
Registered Member
Join Date: Jun 2011
Posts: 820
|
|
12/03/2015, 08:17 PM | #17 | |
Registered Member
Join Date: Feb 2003
Location: Pittsburgh
Posts: 20,772
|
Quote:
|
|
12/03/2015, 08:18 PM | #18 |
Registered Member
Join Date: Mar 2015
Posts: 940
|
My three tanks (10g, 29g and 56g) have spent about 40 hours running off my Honda 3kw over the last month. That's three separate storms. It's also a whole bunch of extension cords!
|
12/03/2015, 09:15 PM | #19 | |
RC Mod
|
Quote:
__________________
Jesse I'm not saying I'm Batman. I'm just saying nobody has ever seen me and Batman in a room together. |
|
12/04/2015, 08:07 AM | #20 |
Registered Member
Join Date: Feb 2003
Location: Pittsburgh
Posts: 20,772
|
Generac still builds nice standby and prime equipment over 20kW but their consumer air cooled stuff is marginal, at best. Sadly, the same holds true for almost all of the sub 20kW stuff anymore. In fact, most of it is the same stuff shoved into different tin.
In the meantime, I ordered one of those conversion kits for my HF special tri-fuel. Will let you know how it works. |
12/04/2015, 08:55 AM | #21 |
Registered Member
Join Date: Jan 2015
Posts: 1,598
|
Thank you guys for the valuable info. I didn't know that I need an inverter to run electronics. I am glad I asked.
I like Honda, but they are very expensive. I understand that they are better quality, but I can't justify the cost. I live in the city limit, and we rarely get power outage, so I probably will not get much use out the generator. It is a safety net just in case. Is Champion a good brand? I found this one on Costco website. "Pure Sine Wave – less than 5% THD (total harmonic distortion) – safe to run sensitive electronics" (is this good enough) http://www.costco.com/Champion-3%2c5...100139455.html
__________________