Ok I have 1 dedicated 20amp breaker for my tank on a gfi circut. I just got my MH fixture today. Odyssea 72" with 250w MH. 4x96w PC. with that and an ASM skimmer, viaaqua2900, 48" 260w PC for refigium and 2 smaller powerheads.
Am I overloading the circut? The gfi just tripped and nothing was wet. I reset and off we went. How many amps ruffly is all that? any electrical guru's that can chime in?
__________________
Can't fix stupid Current Tank Info: 180g Acrylic, mixed reef, 55 fuge,DSB, |
02/23/2007, 06:10 PM | #2 |
Moved On
Join Date: Jan 2002
Location: NW Phoenix
Posts: 16,621
|
Here is a link to the electrical calculator on the RC home page, you can figure it yourself.
http://reefcentral.com/calc/tank_elec_calc.php Tripping a GFI and tripping a circuit breaker are two entirely different things, one is a ground fault or electrical leakage into the tank and the other is an overloaded circuit. |
02/23/2007, 06:52 PM | #3 |
Registered Member
Join Date: Sep 2006
Location: Sheboygan, WI
Posts: 309
|
I guess I was more curious as to the amperage I was pulling. The breaker did not trip just the gfi. And nothing was wet. I reset and off we go. Appreciate that link tho! thanks
__________________
Can't fix stupid Current Tank Info: 180g Acrylic, mixed reef, 55 fuge,DSB, |
02/23/2007, 06:56 PM | #4 |
Moved On
Join Date: Jan 2002
Location: NW Phoenix
Posts: 16,621
|
If you add up all your wattage and divide by 120 that will give you your amperage. You did not provide the watts on all the equipment so only you can figure it.
|
02/23/2007, 07:34 PM | #5 |
Registered Member
Join Date: Sep 2006
Location: Sheboygan, WI
Posts: 309
|
thats kinda what i was looking for ...thanks!! I'm pulling 18amps on a 20 amp circut. a little too much id say eh?
Also can I put a 20 amp gfi instead of the 15amp thats installed? The breaker is a 20 amp breaker..... thanks in advance
__________________
Can't fix stupid Current Tank Info: 180g Acrylic, mixed reef, 55 fuge,DSB, Last edited by Jorgens; 02/23/2007 at 07:40 PM. |
02/23/2007, 07:57 PM | #6 |
Premium Member
Join Date: Nov 2004
Location: Moncton, NB Canada
Posts: 309
|
well some of your issues is to know the gauge of your wiring as well. If you try and run a 20 or 30 Amp circuit breaker on 15 Amp wire you will possible have overheating in your wires.. especially if you are drawing 18 amps as it is.
Can you run another dedicated line? |
02/24/2007, 09:56 AM | #7 |
Registered Member
Join Date: Sep 2006
Location: Sheboygan, WI
Posts: 309
|
I'm not an electrician but I believe it's 12g wire
__________________
Can't fix stupid Current Tank Info: 180g Acrylic, mixed reef, 55 fuge,DSB, |
02/24/2007, 09:57 AM | #8 |
Registered Member
Join Date: Sep 2006
Location: Sheboygan, WI
Posts: 309
|
As for another dedicated line no. the box is full. However I could borrow from say the bedroom/hallway lights. thats on it's own 15amp. The living room has it's own 15amp. only thing there is the TV which is never on cause we watch the fish..lol
This isn't anything id try myself. But I'd like to give the electrician more info on what it is we do. Most can't fathom that a tank need THAT much electricity....