I read a thread about a guy with a 120 acrylic tank in a NY City apartment. He had an inline chiller for his set up, but swapped it out for a drop in. He feels that drop in chillers are more efficient than in line chillers. Based on my brief searching on the web, I'm inclined to agree with him.

Pro's:

Drop in chillers dont require an external pump to feed them. This means less power is used overall. This also means no heat added from another pump to the system.

Con's:

Drop in chillers only have a 5 foot cable for the heat exchanger, so you are limited in where you can place them. If you have an enclosed stand, you're going to need to vent the heat from the chiller somewhere, or you'll wind up re-heating your water from the (now) higher ambient air temperature.

This guy's solution to this was to (possibly) run a dryer duct vent from the rear of this chiller to somewhere else. Seems plausible, but possibly unsightly.

Thinking about this made me reevaluate what I'm doing with my tank and what I want to do for an upcoming upgrade. I currently have a 75 gallon (total water volume) system with dual 250 watt DE MH's, an Iwaki 55RLT running through an OM 4 way for circulation, and PCH CL-650 1/4 hp chiller fed by an Iwaki 40RLT. To my knowledge, the three biggest energy users in reefkeeping are lights, pumps, and chillers. If I can reduce 2 of the 3, I figure I can minimize the impact of my tank on my electrical bill. This becomes more important with a bigger tank.

Checking things out online, (information supplied by manufacturers), the Cyclone TrimLine 1/3HP Drop-In Chiller uses 7.2 amps of power and will remove 4050 BTU's from a tank.

By way of comparison, my CL-650 draws 5.8 amps, and removes 3000 BTU's.
CL-650 1/4HP Aquarium Chiller unit. You have to click on the instructions link (PDF) and then eyeball closely to see the power usage in the first thumbnail.
Factoring in my Iwaki 40RLT adds another 1.3 amps. So I'm running 7.1 amps to chill my modest 75 gallon system, when I can run 7.2 amps and chill 250 gallons...which is my target system volume.

Thoughts, comments, experiances??? Please give your input here as I'm trying to be as energy efficient as possible.

Nick


__________________
A good friend will come and bail you out of jail...but, a true friend
will be sitting next to you saying, "Damn, that was fun!"
maxxII is offline   Reply With Quote
Unread 03/29/2006, 04:06 PM   #2
Julio
Registered Member
 
Julio's Avatar
 
Join Date: Feb 2002
Location: New york
Posts: 7,978
The only reason why they would be more effecient is that they are less of a hassle to clean, but inline chillers are more effecient in cooling.


__________________
Thanks, Have a nice day.
Julio

Current Tank Info: 90 gallon reef w/ 250 watt SE XM10Ks and AP1003, 12 gallon reef, 40 gallon reef
Julio is offline   Reply With Quote
Unread 03/29/2006, 04:48 PM   #3
infrared69
Registered Member
 
Join Date: Apr 2003
Location: wyoming, pa
Posts: 587
why dont you use the pump from your closed loop or your return pump to run thru the chiller?


__________________
The quickest way to end a war is to lose it.

Current Tank Info: 95g, 2x250w MH Phoenix 14K D/E, SLS Reef Optix III, BlueWave VII HQI Ballast, 55g Sump, ASM G-3 Skimmer, Red Sea 100mg Ozonizer Deluxe, Nilsen Reactor, Typhoon III RO/DI
infrared69 is offline   Reply With Quote
Unread 03/29/2006, 06:26 PM   #4
maxxII
Super Housemonkey!
 
maxxII's Avatar
 
Join Date: Apr 2003
Location: St Louis Mo
Posts: 4,442
I am using my return pump to feed the chiller. If I tap into the closed loop pump, then I'll lose flow from the closed loop which I'm unwilling to do at this point in time.

Julio, How did you arrive at this conclusion? Not trying to pic a fight, just trying to figure out your source of information.

This chiller uses the same amperage and removes the same BTU's as its drop in sibling.

Delta TrimLine 1/3HP In-Line Chiller
VS
Cyclone TrimLine 1/3HP Drop-In Chiller

If one were more efficent than the other, wouldnt it draw less amperage or remove more BTU's? I realize the efficiency could be in frequency of cycling on/off...but unless someone has recorded the two under similar conditions, its pretty hard to determine...

Like I said, I'm not trying to pick a fight, just seeking solid information. Thanks in advance.

Nick


__________________
A good friend will come and bail you out of jail...but, a true friend
will be sitting next to you saying, "Damn, that was fun!"
maxxII is offline   Reply With Quote
Unread 03/29/2006, 07:49 PM   #5
RobbyG
Registered Member
 
RobbyG's Avatar
 
Join Date: Jun 2005
Location: 600 Ft From the Reef
Posts: 2,099
I am also wondering how you came to this conclusion, not picking an argument, it's just I have heard it the other way around and I am wondering where you got this info?

Quote:
Originally posted by Julio
The only reason why they would be more effecient is that they are less of a hassle to clean, but inline chillers are more effecient in cooling.



RobbyG is offline   Reply With Quote
Unread 03/29/2006, 09:09 PM   #6
infrared69
Registered Member
 
Join Date: Apr 2003
Location: wyoming, pa
Posts: 587
i would also tnd to agree with inline being the better of the two. i have not yet purchaseda chiller for my setup, but with my sump in the basement, i think i will be adding a inline chiller and using my return pumps to do all the work. also, after thinking about my last post you probably cant use your CL pump, the flow rate would exceed maxium and not make for good heat transfer/


__________________
The quickest way to end a war is to lose it.

Current Tank Info: 95g, 2x250w MH Phoenix 14K D/E, SLS Reef Optix III, BlueWave VII HQI Ballast, 55g Sump, ASM G-3 Skimmer, Red Sea 100mg Ozonizer Deluxe, Nilsen Reactor, Typhoon III RO/DI
infrared69 is offline   Reply With Quote
Unread 03/29/2006, 09:11 PM   #7
Julio
Registered Member
 
Julio's Avatar
 
Join Date: Feb 2002
Location: New york
Posts: 7,978
Drop in chillers don't run water through a chamber or in the case of chillers a heat exchanger that a drop in chiller wont' do, it will cool the water aroudn the probe offcourse it is a proven fact that inline chillers have proven to work better through the years.
There was a big debate on this about 1 or 2 summers ago, do a search on RC.


__________________
Thanks, Have a nice day.
Julio

Current Tank Info: 90 gallon reef w/ 250 watt SE XM10Ks and AP1003, 12 gallon reef, 40 gallon reef
Julio is offline   Reply With Quote
Unread 03/29/2006, 11:05 PM   #8
maxxII
Super Housemonkey!
 
maxxII's Avatar
 
Join Date: Apr 2003
Location: St Louis Mo
Posts: 4,442
I did one and found several threads, several that you were on, but none that proved or showed why inlines were more efficient than drop ins.

I understand what you're saying...there is more water volume in contact with the probe/heat exchanger, but how is that any different from cooled water from the inline heat exchanger being returned to your tank? You dont want a jet or stream of cold water entering your tank, the object is cooler water...which will disperse throughout the water column.

Do you have a link to this thread or any keywords for another search?

Nick


__________________
A good friend will come and bail you out of jail...but, a true friend
will be sitting next to you saying, "Damn, that was fun!"
maxxII is offline   Reply With Quote
Unread 03/29/2006, 11:15 PM   #9
maxxII
Super Housemonkey!
 
maxxII's Avatar
 
Join Date: Apr 2003
Location: St Louis Mo
Posts: 4,442
The Cyclone TrimLine 1/3HP Drop-In Chiller uses 7.2 amps of power and will remove 4050 BTU's from a tank.

My CL-650 draws 5.8 amps, and removes 3000 BTU's.

Looking at the two examples, the Cyclone gets 562.5 btu's per amp and my inline gets 517 per amp. Purely based on the manufacturer claims you're looking at about 10% better efficiency factor on the drop in chiller.

This doesnt prove much, just that the larger Cyclone is more efficient than the smaller PCH. There may be more efficient inline chillers out there. This is the kind of information I'm looking for.

Nick


__________________
A good friend will come and bail you out of jail...but, a true friend
will be sitting next to you saying, "Damn, that was fun!"
maxxII is offline   Reply With Quote
Unread 03/30/2006, 08:28 AM   #10
Julio
Registered Member
 
Julio's Avatar
 
Join Date: Feb 2002
Location: New york
Posts: 7,978
Hey Nick,
i tried doing a search myself and keeps on saying the search engine is diabled. YOu dont' have to shoot the cold water back into your tank directly, i don't i have it mixed with the draining water from the tank to cool the tank at a much slower rate and not shock the corals.


__________________
Thanks, Have a nice day.
Julio

Current Tank Info: 90 gallon reef w/ 250 watt SE XM10Ks and AP1003, 12 gallon reef, 40 gallon reef
Julio is offline   Reply With Quote
Unread 03/30/2006, 08:43 AM   #11
samsfishnchips
Premium Member
 
samsfishnchips's Avatar
 
Join Date: May 2004
Location: New Jersey
Posts: 2,328
maxxII,

if possible I would go with drop, no playing around with flow rates, no pump that can fail,

and to me, more efficient, why

no need to add another pump, some cases,
water cooled right in the sump, no need for lines running outside

inline, would be preferred is no space, chiller can relocated a bit away and the heat of it too,

be careful of and take proper precautions, specially when hot

pump feeding chiller die
I believe my tank is dead.

"chiller trip the breaker for some unknown reason."
Worse Week Of My Life

good luck with your choice,

sam


__________________
Every moment is a chance for happiness.

Current Tank Info: 90G 99% SPS
samsfishnchips is offline   Reply With Quote
Unread 03/30/2006, 09:48 AM   #12
Fliger
Registered Member
 
Fliger's Avatar
 
Join Date: Feb 2003
Location: Chandler, AZ
Posts: 8,642
I don't know much about BTU's - but I can tell you that my drop-in chiller kept my tank cool very quickly and efficiently. I'm not a fan of plumbing and an extra pump so I wanted a drop-in. As long as its in the sump in a high flow area, you're good. Unfortunately the cooling element on my chiller might be too large for my new sump so I might need a new one. ;-( I'm probably going to find a drop-in with the smallest drop-in.

I bought this one (used).

http://www.reefcentral.com/forums/sh...anetics+dropin


__________________
Growing old is mandatory, growing up is optional.
Closed minds should come with closed mouths.

When life hands you lemons, add vodka!

Current Tank Info: Current: 210G Elos System, 2x400W + 6x54W Photon w/Aquaconnects, H&S skimmer, Deltec FR509/ROWAphos+Elos Carbon, 6101's and 6201's, Ocean GEOtronic 900 Chiller/Heater, Biotopus II Controller w/SMS. Elos System 70.
Fliger is offline   Reply With Quote
Unread 03/30/2006, 09:53 AM   #13
golfish
Team RC Member
 
golfish's Avatar
 
Join Date: Oct 1999
Location: Alta Loma, Ca
Posts: 6,776
IME, you want to have the chiller as far away from the tank as you can get it. If you can locate the drop in chiller outside or in another area like you can an inline chiller then it would make adding a chiller a little easier. I have had my chiller outside on the front porch and now in my garage. I also had it in a crawls space under the house that wasn't very big (4x4x2). The chiller didn't get good air flow around it down there so it didn't work very well.

A drop in is much easier to use but for the most parts its going to be less efficient, the main reason being that most people will have it located in an area where it wont get the proper air flow and or it will throw unwanted heat in the tank area.

I have read about people running the lines for a drop in chiller through walls. That's a good option.

Quote:
if possible I would go with drop, no playing around with flow rates, no pump that can fail,
and to me, more efficient, why

no need to add another pump, some cases,
water cooled right in the sump, no need for lines running outside

Most people use a return pump so there's no need to add one.

I'd go find somebody who has a chiller that's running and see how much heat it puts out before you decide. If you feel the heat wont be an issue then your options are greater.


golfish is offline   Reply With Quote
Unread 03/30/2006, 10:12 PM   #14
maxxII
Super Housemonkey!
 
maxxII's Avatar
 
Join Date: Apr 2003
Location: St Louis Mo
Posts: 4,442
The points about the chiller heating up the air surrounding the sump are very valid. IMO this is the biggest drawback to drop in chillers. However, this is also a consideration for in-line chillers as well.

My intent in starting this thread was to attempt to determine if one style of chiller was more effiecient than the other. I realize there are some circumstances unique to each set up that will alter or make one style better suited to a tank than the other.

In my case, the upgrade this is being planned for is a 120 inwall, with a total target volume of 250 gallons after sump and frag tank are plumbed in. The tank and sump, (and consequently chiller) will be on the unfinished side of my basement. This means that with adequate venting, a drop in chiller will be suitable for my needs. This doesnt mean an inline is out of the question, I'm obviously going to have to search and read up on manufacturer's specs regarding power usage etc and compare various chillers against each other to determine whats best for my needs.

One thing I have determined is that my current set up, (CL-650 w/ Iwaki 40RLT) isnt as efficient as the larger cyclone drop in chiller would be.

Cyclone uses 7.2 amps and removes 4050 BTU's.
My set up uses 7.1 amps and only removes 3000BTU's.

30% more BTU's removed for 1/10th more energy used is worth considering.

Nick


__________________
A good friend will come and bail you out of jail...but, a true friend
will be sitting next to you saying, "Damn, that was fun!"
maxxII is offline   Reply With Quote
Unread 03/30/2006, 10:50 PM   #15
RobbyG
Registered Member
 
RobbyG's Avatar
 
Join Date: Jun 2005
Location: 600 Ft From the Reef
Posts: 2,099
The argument of how the drop in chiller is located is valid, but with proper planning the upside is that the drop in can provide a more effiecent cooling system with less chance of something going wrong. The only real downside I see with them is that they tend to be more delicate units because of the potential to damage the hose by bending it too much. Of course the upside to that same flexible hose is that the whole unit can easily be moved to another tank if it's needed in an emergency.


__________________
The Optimist says the glass is half full, the Pessimist says it’s half empty, an engineer only see's a glass that’s twice as big as it needs to be!

Current Tank Info: Insanely Automated Low Power Consumption 90 Gal Oceanic Bow System/Aquatronica Touch Controller/AQ Dosing Pump/AQT LEDS/AQ SMS/Seq Dart Pump/ASM G3/Ozotech Ozonizer/Koralin 1502/Chiller/Typhoon3 Ro/S.Squirt /Phos React/Rmt DSB
RobbyG is offline   Reply With Quote
Unread 03/30/2006, 10:54 PM   #16
maxxII
Super Housemonkey!
 
maxxII's Avatar
 
Join Date: Apr 2003
Location: St Louis Mo
Posts: 4,442
Good point on the flexible hose being somewhat delicate. Hadnt thought along those lines, but I would think once the chiller was set up, you wouldnt mess with it too much?

Nick


__________________
A good friend will come and bail you out of jail...but, a true friend
will be sitting next to you saying, "Damn, that was fun!"
maxxII is offline   Reply With Quote
Unread 03/30/2006, 11:23 PM   #17
RobbyG
Registered Member
 
RobbyG's Avatar
 
Join Date: Jun 2005
Location: 600 Ft From the Reef
Posts: 2,099
True but you never know! One day I left my sump door open for 10 minuts, only to find my 5 year old son pulling the hose out of the sump, the angle he had the hose at just about stopped my heart. Luckily it did not get crimped


__________________
The Optimist says the glass is half full, the Pessimist says it’s half empty, an engineer only see's a glass that’s twice as big as it needs to be!

Current Tank Info: Insanely Automated Low Power Consumption 90 Gal Oceanic Bow System/Aquatronica Touch Controller/AQ Dosing Pump/AQT LEDS/AQ SMS/Seq Dart Pump/ASM G3/Ozotech Ozonizer/Koralin 1502/Chiller/Typhoon3 Ro/S.Squirt /Phos React/Rmt DSB
RobbyG is offline   Reply With Quote
Unread 04/01/2006, 09:17 PM   #18
maxxII
Super Housemonkey!
 
maxxII's Avatar
 
Join Date: Apr 2003
Location: St Louis Mo
Posts: 4,442
I was just pointed towards these chillers....

Current USA Prime Inline Chillers.

Current USA Prime Drop in Chillers.

Current USA Prime Tower Chillers.

Quick math on Amps vs BTU's removed by the Current USA chillers...

Prime Modular and Drop in 1/4 hp.....595.75 BTU's per amp.
Prime Modular and drop in 1/3 hp.....610.52 BTU's per amp.

But the big winners are the new Tower chillers.

Prime Tower 1/3 hp unit.....1000 BTU's per amp
Prime Tower 1/4 hp unit.....1120 BTU's per amp

Marine Depot sells Current USA chillers, and so does Marine and Reef and Gina's.....

Has anyone heard anything about these? I've tried using the RC Google Search, but still cant find much about these.

Anyone have more info?

Nick


__________________
A good friend will come and bail you out of jail...but, a true friend
will be sitting next to you saying, "Damn, that was fun!"
maxxII is offline   Reply With Quote
Unread 04/01/2006, 09:45 PM   #19
golfish
Team RC Member
 
golfish's Avatar
 
Join Date: Oct 1999
Location: Alta Loma, Ca
Posts: 6,776
Quote:
Originally posted by maxxII
The points about the chiller heating up the air surrounding the sump are very valid. IMO this is the biggest drawback to drop in chillers. However, this is also a consideration for in-line chillers as well.

If you were to consider the heat released by a in line chiller a drawback, all you would have to do is move it to another location, there's not much option with a drop in. That said, there have been some good threads about people making cooling barrels, heat excahangers using drop in chillers.

IME, You really have to consider the area the chiller is located, if there's not good air circulation the chiller isn't go to be very efficient no matter if its a drop in or in line.

Both have pro's and con's..the in line can be more efficient but then you have to plumb 30 feet of 1.5" PVC


golfish is offline   Reply With Quote
Unread 04/02/2006, 06:15 PM   #20
RobbyG
Registered Member
 
RobbyG's Avatar
 
Join Date: Jun 2005
Location: 600 Ft From the Reef
Posts: 2,099
Huh!! Wouldnt 30 feet of PVC add more contact time and transfer more heat from the ambient air into the water in the pipe?

Quote:
Originally posted by golfish
Both have pro's and con's..the in line can be more efficient but then you have to plumb 30 feet of 1.5" PVC



RobbyG is offline   Reply With Quote
Unread 04/02/2006, 06:43 PM   #21
golfish
Team RC Member
 
golfish's Avatar
 
Join Date: Oct 1999
Location: Alta Loma, Ca
Posts: 6,776
Quote:
Originally posted by RobbyG
Huh!! Wouldnt 30 feet of PVC add more contact time and transfer more heat from the ambient air into the water in the pipe?
Why would the ambient air be hot


golfish is offline   Reply With Quote
Unread 04/02/2006, 09:38 PM   #22
maxxII
Super Housemonkey!
 
maxxII's Avatar
 
Join Date: Apr 2003
Location: St Louis Mo
Posts: 4,442
Plastic also wont transfer heat very well. I'd be more concerned about whatever pump was needed to push water through 30 feet of PVC adding heat to the water than the ambient air temp.

Nick


__________________
A good friend will come and bail you out of jail...but, a true friend
will be sitting next to you saying, "Damn, that was fun!"
maxxII is offline   Reply With Quote
Unread 04/03/2006, 05:03 AM   #23
golfish
Team RC Member
 
golfish's Avatar
 
Join Date: Oct 1999
Location: Alta Loma, Ca
Posts: 6,776
Quote:
Originally posted by maxxII
Plastic also wont transfer heat very well. I'd be more concerned about whatever pump was needed to push water through 30 feet of PVC adding heat to the water than the ambient air temp.

Nick
No worries, the chiller only runs when the lights come on.


golfish is offline   Reply With Quote
Unread 04/03/2006, 01:40 PM   #24
RobbyG
Registered Member
 
RobbyG's Avatar
 
Join Date: Jun 2005
Location: 600 Ft From the Reef
Posts: 2,099
Its 98 deg outside on a summer day, your tank is at 78 deg that means the Ambient air is 20 deg hotter than your water so when you run 78 deg water through 30 feet of pipe that is surrounded by 98 deg heat, some of that heat is going to transfer to the water in the pipe! The longer the pipe the more heat it will pickup. BTW even plastic pipe transfers some heat.

In any case how does this statement apply

"The in line can be more efficient but then you have to plumb 30 feet of 1.5" PVC "

If anything I can only see how this would make it less efficient


Quote:
Originally posted by golfish
Why would the ambient air be hot



RobbyG is offline   Reply With Quote
Unread 04/03/2006, 03:37 PM   #25
golfish
Team RC Member
 
golfish's Avatar
 
Join Date: Oct 1999
Location: Alta Loma, Ca
Posts: 6,776
Quote:
Originally posted by RobbyG
not picking an argument,

I think you are


Quote:
Originally posted by RobbyG
Its 98 deg outside on a summer day, your tank is at 78 deg that means the Ambient air is 20 deg hotter than your water so when you run 78 deg water through 30 feet of pipe that is surrounded by 98 deg heat, some of that heat is going to transfer to the water in the pipe! The longer the pipe the more heat it will pickup. BTW even plastic pipe transfers some heat.

what the hec are you talking about? who said my lines ran outside? besides, going with your idea, running long lines outside would be better because 90% of the times its cooler then 78 degrees Hec, I could get rid of my chiller

Relax, you don't need to be on the defense so much, your jumping to conclusions.


golfish is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On



All times are GMT -6. The time now is 12:29 AM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
Powered by Searchlight © 2025 Axivo Inc.
Use of this web site is subject to the terms and conditions described in the user agreement.
Reef CentralTM Reef Central, LLC. Copyright ©1999-2022
User Alert System provided by Advanced User Tagging v3.3.0 (Pro) - vBulletin Mods & Addons Copyright © 2025 DragonByte Technologies Ltd.