I am getting ready to wire my VHO retro into my hood. My question is this: Can I use stranded wire opposed to a solid wire for the endcaps. I have bought some wire that is water proof, but it is stranded, not solid. When I used these for my last tank, I used solid strand wire, because that is what I had laying around.
Just don't want to screw anything up! Thanks, Ron
__________________
Ronnie 60g cube - Ghost Overflow - ATI 8 bulb dimmable sunpower - Apex - MP10s - Synergy sump |
![]() |
![]() |
![]() |
#2 |
Registered Member
![]() Join Date: Apr 2008
Location: Grove City, Ohio
Posts: 10,806
|
as long as it is the same gauge, i would not think it makes a difference, but im no electrician!
__________________
I'll try to be nice if you try to be smarter! I can't help that I grow older, but you can't make me grow up! Current Tank Info: 120 mixed reef with 40b sump, RO 150 skimmer, AI Sol Blue x 2, and a 60g Frag Tank with 100g rubbermaid sump. 2 x Kessil A360w lights, BM curve 5 skimmer |
![]() |
![]() |
![]() |
#3 |
Moved On
Join Date: Jan 2002
Location: NW Phoenix
Posts: 16,621
|
Stranded will not stay tight in the stab connectors of the endcaps and may pull loose and cause a fire.
Get the correct solid wire in the correct gauge and do it right the first time would be my advice. |
![]() |
![]() |
![]() |
#4 |
Professional Stick Gluer
![]() Join Date: Nov 2003
Location: NW Arkansas
Posts: 2,216
|
Thanks AZ...That is what I was thinking, but I wanted confirmation.